acoustical liner

Status
Not open for further replies.

mech4321

Mechanical
Jun 8, 2009
14
I will install a liner in the first 10 feet of supply (10 tons, split system). Should I do the same in the ducted return?
 
Replies continue below

Recommended for you

Need further input.

Is it (split system) a draw-through or blow-through fan?

Does it have a return fan?
 
I'd line the return and not the supply. Supply you should consider a sound attenuator instead. Porous liners can become microbial farms with cycling of the cooling coil or humidification.
 
"microbial farms' I like that one



The way we build has a far greater impact on our comfort, energy consumption and IAQ, than any HVAC system we install
 