Acoustical roof deck with cover plate

Status
Not open for further replies.

DETstru

Structural
Nov 4, 2009
395
I'm working on a project where the architect wants to use an acoustical roof deck with a factory installed cover plate (see the attached detail).

I'm having trouble contacting the manufacturer and I need to know, how will this get attached to the structure? The cover plate is in the way for screwing/shooting the deck down. Anybody have an idea of how this is done?
 
 http://files.engineering.com/getfile.aspx?folder=5d94e20c-0ffb-49be-95b6-fc4bbd9a115e&file=_FLAT_PL.pdf
Replies continue below

Recommended for you

Your attachment is upside down from how I've usually seen it for structural deck. Usually the acoustical filler is in the downwards facing flutes with cover plate on the bottom and then you attach to structure just like you would a normal deck with the only exception being you have to fasten through both deck and cover plate instead of just through deck.

Vulcraft Cellular Deck Website
 