What is typically the maximum permissible temperature rating of bushing cable terminations (breakers, isolators, CTs, trafos) in substations? I'd like to bring ACSS into the substation.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
NEMA Standard CC-1, ANSI/IEEE Standard C119 :
a) The ratings on Table are given for a wind velocity of 2 ft/s, an ambient air temperature of 40C, a conductor temperature of 70C (30C rise), and emissivity 0.35. Sun effect was not taken into consideration because of the wide variation depending upon the location.
b) The designer should recalculate these values to take sun effect into consideration once the installation location is determined.
c)The temperature rise shall be determined at 100, 125, and 150% of the rated current
d) is not intended to qualify the connectors for service higher than the normal rating.
e) Connectors that are supplied in equipment are covered by the equipment standards and are excluded from this standard.
f) If the user desires to operate the conductor and connectors at a higher temperature rating, the test currents shall be raised to a value agreed upon between the manufacturer and user.