Should the ceilings in a hospital have an importance factor = 1.5 with regards to ASCE chapter 13 calculations? From section 13.1.3, the Ip is 1.5 for:
"The component is in or attached to a Risk Category IV
structure, and it is needed for continued operation of the
facility or its failure could impair the continued operation
of the facility."
I would figure that the ceiling collapsing would qualify an Ip of 1.5 (same for partition walls).
But I am reviewing OSHPD OPD document for suspended ceilings and trying to back calculate what they used for their wire strength.
(
For a 144 sq ft area shown on page CL2.22, the max Sds is 1.15. I calculate an ASD brace wire force of 472 lbs at Ip = 1.5 and 315 lbs for Ip = 1.0. This does not compute with what I think a 12 ga. wire strength is. A 70 ksi 12 ga. wire (0.106") should be 618 lbs. Using a reduction factor of 2 means an allowable strength of 309 lbs. The 2 reduction factor isn't listed in the OPD but is listed in the DSA IR 25-1. IR 25-2 also uses the same charts for Sds and bracing area. Which leads me to believe the OSHPD document does not set the ceiling importance factor = 1.5! Am I off base here?
DSA publications (
"The component is in or attached to a Risk Category IV
structure, and it is needed for continued operation of the
facility or its failure could impair the continued operation
of the facility."
I would figure that the ceiling collapsing would qualify an Ip of 1.5 (same for partition walls).
But I am reviewing OSHPD OPD document for suspended ceilings and trying to back calculate what they used for their wire strength.
(
For a 144 sq ft area shown on page CL2.22, the max Sds is 1.15. I calculate an ASD brace wire force of 472 lbs at Ip = 1.5 and 315 lbs for Ip = 1.0. This does not compute with what I think a 12 ga. wire strength is. A 70 ksi 12 ga. wire (0.106") should be 618 lbs. Using a reduction factor of 2 means an allowable strength of 309 lbs. The 2 reduction factor isn't listed in the OPD but is listed in the DSA IR 25-1. IR 25-2 also uses the same charts for Sds and bracing area. Which leads me to believe the OSHPD document does not set the ceiling importance factor = 1.5! Am I off base here?
DSA publications (