Actual Burden at the secondary of the VT

Status
Not open for further replies.

NickParker

Electrical
Sep 1, 2017
420
The actual burden at the secondary of the voltage transformer (VT) is 5VA, However the supplied VT has 15VA. Would this cause any problem?
 
Replies continue below

Recommended for you

No

I'm assuming this is a unit produced to IEC standard. If so, that standard specifies that the rated accuracy is to be maintained from 25%-100% of the rated burden.

 
Dear Mr NickParker

Q. " The actual burden at the secondary of the voltage transformer (VT) is 5VA, However the supplied VT has 15VA. Would this cause any problem? "
A. The VT are usually rated 10, 15, 25VA... As for your case, the burden (5VA) is [lower than] the VT (15VA). It [should not] cause any problem.
We can study it in detail if you can tell us what is your concern/application? What is the load and the VT Class?
BTW: IEC 61869-x series replace IEC 60044-x series.

Che Kuan Yau (Singapore)
 
Your vendor is answering a question about a CT, not about your VT. 5VA burden on your VT should be no problem.
 
My bad. Actually my question is regarding CT; due to my absent mindedness, I posted as VT.

Sorry Gentlemen!
 
My answer above holds true for CTs as well.

 
Dear Mr NickParker

" Actually my question is regarding CT; due to my absent.... The vendor .. .. reply is in the attachment"
Your vendor has given you an excellent reply. Do you have any more doubts/problems?
See che12345 12 Nov 19:
We can study it in detail if you can tell us what is your concern/application? What is the load and the CT Class?
BTW: IEC 61869-x series replace IEC 60044-x series.CT

Che Kuan Yau (Singapore)
 