rockman7892
- Apr 7, 2008
- 1,165
We are currently looking into replacing/modifying some 230kV OH bus in a customer owned substation and in the process of doing so I was wondering if it made sense to add bus differential to the OH bus system.
The attached One-Line shows the existing 230kV OH customer owned bus being fed by two incoming breakers (52-1 & 52-2) which are supplied by a local utility transmission line. All breakers and bus shown on the one-line are owned by customer, with the utility having a line differential circuit wrapping on the load side of each breaker going back to their local switchyard in close proximity.
Currently the only bus protection resides with 50/51 settings in the 52-1 & 52-1 breaker relays with the Instantaneous setting set with no delay, but above the secondary let though current of any of the transformers in order to avoid nuisance tripping for secondary faults. I'm curious to hear weather or not that instantaneous setting is considered adequate protection for the bus or if adding a buss differential would add significant protection? There are a number of spare CT's already available for use that are currently wired back to the main substation control panel. It would likely just be a matter of adding a relay to existing panel, connecting CT's, and integrating necessary controls.
Interested in hearing others thoughts