- Oct 10, 2007
- 9
Hi,
I am working on a project to add a 480V delta feeder panel to an existing 480V delta main panel at an industrial type warehouse. The main panel (mlo) is being fed by three single phase 167KVA transfomers which means that they are rated to supply 602 amps total. I know the current setup is to code because if I sum up all the breakers on the main panel and multiply them by 80% I come up with a number less than 602 amps (because they should be sized at 125% of their load). My problem is that if I add a 125 amp breaker to the panel I now exceed the 602 amps. Since there are no load calculations for the facility I have no idea what to do. Any suggestions? Is there a rule of thumb I can use so that I can avoid having to perform load monitoring?
I am working on a project to add a 480V delta feeder panel to an existing 480V delta main panel at an industrial type warehouse. The main panel (mlo) is being fed by three single phase 167KVA transfomers which means that they are rated to supply 602 amps total. I know the current setup is to code because if I sum up all the breakers on the main panel and multiply them by 80% I come up with a number less than 602 amps (because they should be sized at 125% of their load). My problem is that if I add a 125 amp breaker to the panel I now exceed the 602 amps. Since there are no load calculations for the facility I have no idea what to do. Any suggestions? Is there a rule of thumb I can use so that I can avoid having to perform load monitoring?