etbrown4
Mechanical
- Apr 16, 2012
- 19
Adding a 6 circuit 30a transfer switch, connecting to main panelboard.
Requires a 12g thhn out to the transfer switch and back to main panel for each circuit.
Plan to run those 12 conductors in one conduit.
Plan to run 10g neutral and ground in a separate cable from main panel to transfer switch.
Nec typically requires current carring conductors and neutrals to run in the same raceway.
Transfer switch manufacturer says conductors and neutrals not required to be in same raceway, but they are not the Nec!
Mfg says this setup will work properly so long as there is a 10g neutral connecting transfer switch and main panel.
Can the conductors and neutral be safely be run separately?
Requires a 12g thhn out to the transfer switch and back to main panel for each circuit.
Plan to run those 12 conductors in one conduit.
Plan to run 10g neutral and ground in a separate cable from main panel to transfer switch.
Nec typically requires current carring conductors and neutrals to run in the same raceway.
Transfer switch manufacturer says conductors and neutrals not required to be in same raceway, but they are not the Nec!
Mfg says this setup will work properly so long as there is a 10g neutral connecting transfer switch and main panel.
Can the conductors and neutral be safely be run separately?