Dear All,
For an existing PSV installed on a vessel and which was designed for fire case at 21% overpressure- orifice area given by vendor was H orifice.. the required area in the original case. Vendor provided a certified ASME capacity of 2400 Kg/hr.. MY DOUBT IS that this should not be at 21% overpressure but shall comply with ASME SEC VIII Div.1 UG-129 of having all certified relieving capacity at 10% overpressure.
as part of validating the existing PSV to handle a blocked outlet scenario.. I saw that the required capacity of 26000 Kg/hr two phase flow but due to the relatively high mass flux estimated using the homogeneous equilibrium method, the size of the existing PSV is found to be G!.
Therefore, my question is:
1- do you agree that the comparison should be based on volumetric flow and NOT mass flow.
2- when evaluating the PSV adequacy.. do we look mainly at the area being adequate since there are other factors that determine the size requirement (not only relieving rate but all gas properties, two phase flux etc).
3- Is it correct that the ASME rated capacity will differ based ont he governing scenarios and hence if my new scenario needs to be compared to the rated capacity of the valve (specially if the gas properties and Temperature are different) I will have to recheck with vendor, because I need to know if my capacity will be within 25% of the rated capacity to avoid chattering.
Vendor reported his coefficient of discharge, the calculated area as per ASME Kd and the selected area based on his valve model but the corresponding calculating maximum ASME capacity which is based on the required capacity of the valve is 2400 Kg/hr against 1818 Kg/hr required capacity. if the scenario changes to blocked outlet as a result of a new revamp but the volumetric rate of the PSV is less than the installed PSV, will I still need to request for the corresponding rated capacity.
Appreciate your views.
Regards,
For an existing PSV installed on a vessel and which was designed for fire case at 21% overpressure- orifice area given by vendor was H orifice.. the required area in the original case. Vendor provided a certified ASME capacity of 2400 Kg/hr.. MY DOUBT IS that this should not be at 21% overpressure but shall comply with ASME SEC VIII Div.1 UG-129 of having all certified relieving capacity at 10% overpressure.
as part of validating the existing PSV to handle a blocked outlet scenario.. I saw that the required capacity of 26000 Kg/hr two phase flow but due to the relatively high mass flux estimated using the homogeneous equilibrium method, the size of the existing PSV is found to be G!.
Therefore, my question is:
1- do you agree that the comparison should be based on volumetric flow and NOT mass flow.
2- when evaluating the PSV adequacy.. do we look mainly at the area being adequate since there are other factors that determine the size requirement (not only relieving rate but all gas properties, two phase flux etc).
3- Is it correct that the ASME rated capacity will differ based ont he governing scenarios and hence if my new scenario needs to be compared to the rated capacity of the valve (specially if the gas properties and Temperature are different) I will have to recheck with vendor, because I need to know if my capacity will be within 25% of the rated capacity to avoid chattering.
Vendor reported his coefficient of discharge, the calculated area as per ASME Kd and the selected area based on his valve model but the corresponding calculating maximum ASME capacity which is based on the required capacity of the valve is 2400 Kg/hr against 1818 Kg/hr required capacity. if the scenario changes to blocked outlet as a result of a new revamp but the volumetric rate of the PSV is less than the installed PSV, will I still need to request for the corresponding rated capacity.
Appreciate your views.