Advice on ATEX

Status
Not open for further replies.

SA07

Electrical
Feb 22, 2018
366
Hi
Following a study done at our power plants we must review some parts. We have an LPG station, 2 LPG burners on a boiler, coal dust, bagasse dust.

Can you plz advise for a valve as attached picture, should all the parts be ATEX near the burner?
1 the limit switch box
2 the positioner
3 the valve

IMG_20210825_114526_htt6ix.jpg


We have been requested to relocate some panels from the burner a few meters away. What will be more economical: to convert the panels to ATEX or relocate them?

IMG_20210825_115122_tatyud.jpg


IMG_20210825_115126_nhhpzo.jpg



Is the distribution box inside an aluminium panel acceptable where there is some dust particle in this zone?


IMG_20210825_133525_oactow.jpg


This zone is classified as Z21, Expected equipment protection level IIIC T185degc
 
Replies continue below

Recommended for you

The safest design is to mount as much equipment as possible outside of hazardous areas. It is also often more economical. Explosion rated equipment is quite expensive.
Dust: Dusty areas may be classified as hazardous by the Canadian code. It depends.
What code governs your work?

--------------------
Ohm's law
Not just a good idea;
It's the LAW!
 
The report was done according to BS EN 60079-10-2.2015
 