mo76
Civil/Environmental
- May 28, 2005
- 2
Hello All,
I am converting (CY) of aggregate (for a road construction project) to (TONS). Does any one have scientific data to use for the density of aggregate base rock?
Several sources state that "most natural" aggregates have particle densities between 150 and 181 (lb/ft^3). In the Civil Engineering Reference Manual (CERM), under chapter 48, "Properties of Concrete and Reinforcing Steel" Pg. 48-2, "Aggregate" states that, "Most sand and rock aggregate has a specific weight of approximately 165 (lb/ft^3).
A common practice of industry professionals is to divide TONS by (2) to get CY. Dividing TONS by (2) to get CY assumes that the in place aggregate will have a density of 148 lb/ft^3. However, a differential of a couple of units (148 vs 165) makes a big difference in cost on big projects. Therefore I thought that somebody must have a more scientific approach to deal with this issue.
The (150-180) density data comes from a "Design and Control of Concrete Mixtures" book and appears to refer to the "particle" density of aggregate. However, since the aggregate is made up of particles, it is reasonable that the compacted density of the aggregate is between (150-180 lb/ft^3).
If you consider an entire road bed compacted at 95%, would it be reasonable to estimate that the density of the aggregate road bed is 165 (lb/ft^3) as stated in the CERM under aggregate properties section?
I am converting (CY) of aggregate (for a road construction project) to (TONS). Does any one have scientific data to use for the density of aggregate base rock?
Several sources state that "most natural" aggregates have particle densities between 150 and 181 (lb/ft^3). In the Civil Engineering Reference Manual (CERM), under chapter 48, "Properties of Concrete and Reinforcing Steel" Pg. 48-2, "Aggregate" states that, "Most sand and rock aggregate has a specific weight of approximately 165 (lb/ft^3).
A common practice of industry professionals is to divide TONS by (2) to get CY. Dividing TONS by (2) to get CY assumes that the in place aggregate will have a density of 148 lb/ft^3. However, a differential of a couple of units (148 vs 165) makes a big difference in cost on big projects. Therefore I thought that somebody must have a more scientific approach to deal with this issue.
The (150-180) density data comes from a "Design and Control of Concrete Mixtures" book and appears to refer to the "particle" density of aggregate. However, since the aggregate is made up of particles, it is reasonable that the compacted density of the aggregate is between (150-180 lb/ft^3).
If you consider an entire road bed compacted at 95%, would it be reasonable to estimate that the density of the aggregate road bed is 165 (lb/ft^3) as stated in the CERM under aggregate properties section?