BronYrAur
Mechanical
- Nov 2, 2005
- 798
I have an AHU supply fan that is drawing too many amps. Don't know particulars, but it is a 40 HP fan on a VFD. I am told that they cannot turn it up past 50 Hz without over-amping. 50 Hz, however, only gives me 20,000 CFM and the system was sized for 24,000 CFM.
Am I correct in thinking that I do NOT have enough static loss in the ductwork and therefore not enough resistance against the fan? If so, can I just throttle back dampers in order to increase the static, which will allow me to go up to 60 Hz and hopefully 24,000 CFM?