remp
Mechanical
- Sep 15, 2003
- 224
I'm installing and AHU to serve 3 floors of production area.
There is a smoke damper on the inlet and discharge side of the AHU, to shut down in fire mode. The inlet of the AHU takes air from a fresh air plenum in another fire compartment. The consultant reckons we need these dampers to shut in fire mode, which is fair enough, but he wants to put a smoke detector at the inlet and another one at the outlet. I think this is a waste, and one would do at the outlet. He reckons because of the presence of filters including a HEPA filter smoke at one end would not reach the other, which I think is incorrect. What do you think/ The consultant keeps on refering to NFPA 90 too. Is he correct?
There is a smoke damper on the inlet and discharge side of the AHU, to shut down in fire mode. The inlet of the AHU takes air from a fresh air plenum in another fire compartment. The consultant reckons we need these dampers to shut in fire mode, which is fair enough, but he wants to put a smoke detector at the inlet and another one at the outlet. I think this is a waste, and one would do at the outlet. He reckons because of the presence of filters including a HEPA filter smoke at one end would not reach the other, which I think is incorrect. What do you think/ The consultant keeps on refering to NFPA 90 too. Is he correct?