Yes, I'm thinking way out of the box here.
The air handlers serving our new lab supply 100% outside air and use steam preheat coils. A face and bypass design was somehow discarded during design and modulating steam valves were used instead. At lower temperatures (10-50degF), the coils are at atmospheric due to the opening of the vacuum breaker downstream of the steam valve. With so little head, condensate sits in the coil waiting to get out the tiny trap orifice. Meanwhile the steam/air mixture above the water cools and the freezestat trips.
My idea before resorting to more expensive options, is to tap into the pipe downstream of the steam valve and add a 5psi or so compressed air supply. The coil already gets induced air from the vacuum break, I'm just trying to give it some oomph to clear the condensate. Crazy??
The air handlers serving our new lab supply 100% outside air and use steam preheat coils. A face and bypass design was somehow discarded during design and modulating steam valves were used instead. At lower temperatures (10-50degF), the coils are at atmospheric due to the opening of the vacuum breaker downstream of the steam valve. With so little head, condensate sits in the coil waiting to get out the tiny trap orifice. Meanwhile the steam/air mixture above the water cools and the freezestat trips.