In lieu of specific manufacturer data, here is what I have used.
1 HP = 746 Watts
Assume 80% efficiency, so each compressor HP = 933 Watts
Add 1/10 HP per compressor HP for dryers or 93 Watts
This totals 1,026 Watts per compressor HP or roughly 3,500 BTUH per compressor HP.
(CFM/HP) = (BTUH/HP)/1.08/Delta-T
Your Delta-T is your allowable or desirable room temperature minus the outside air temp. In other words, if you want to keep the room at 105, and your outside air is 95, then your Delta-T is 10.
Using 10 deg Delta-T, your required CFM/HP is 3,500/1.08/10, or 324 cfm/HP
With a 150HP compressor, you will need 48,600 CFM. This is obviously a truckload for such a small room.