I ran my motor performance program for a motor that we rewound. 1250 HP, 3ph, 4160 V, Ifl 166.8 Amps, 893 rpm.
The rotor OD (outside diameter) is 23.622” and the stator bore diameter 23.750 for a radial air gap of 0.64”.
I ran the program for 125% (0.080”) and 150% (0.96’) air gaps (equivalent to machining the rotor OD) , some of the main motor parameters results are:
0.064 air-gap 0.080” air-gap 0.096” air-gap
Locked rotor Current (amps) 1163 1134 1109
Locked rotor torque (%) 182.8 172.5 163.6
Prim. Leakage react (pu) .077 .076 .075
Sec. Leakage react (pu) .165 .164 .163
No load amps 63.9 71.0 79.5
Full load amps 166.8 171.9 177.2
EFF @ FL (%) 95.41 95.44 95.43
P.F. @ FL (%) 81.24 78.82 76.49
These results do not mean necessarily the same behavior for different motors, since saturation, distance from the cage to the rotor bars, etc could be totally different.