I typically use draw thru's for the reason that Kiwimace mentioned. Blow thru's typically require a diffuser plate of some sort so that the air is more evenly spread over coils, this cause an additional pressure drop. Blow thru's have a built in 'reheat' ability due to the fan heat gain, but that is small. I believe McQuay did a study on the two types of configurations years ago. Both configurations work and designers will argue the pro's and con's of each. It is really up to you. If possible, I would recommend a plug or plenum fan (draw thru) unless your architect gives you a lot of room to get fully developed flow in your duct work before major duct fittings, transitions and related....
If the system is a VAV type and you are actively controlling minimum outside air as per ASHRAE, your mixed air temp could conceivably get cold enough to warrant freeze protection. This would happen w/ fan at minimum and ventilation load at its max. For this reason we typically have a preheat coil in our northern climate. I would check you mixed air condition w/ maximum ventilation load at min fan speed assuming it is a VAV .
Your concern for moisture and possible reheat control in your climate is valid and could be of more concern than the low m.a. temp.
In economizer mode, cold air stratification could cause issues w/ freezing, I would suggest an air blender to help mix the air more evenly before it hits the stagnant cooling coil. Which, like the blow thru diffuser plate causes more pressure drop and significantly more length to your AHU. I have heard the blow thru's help prevent cold air stratification, but I am not convinced of that as I think the cold air goes to the outside of the wheel while the warm air goes on the bottom. Others may have more experience w/ that. Especially those that commission these systems.
I suppose it is possible that you would need both a reheat coil and preheat coil? You may need to check ASHRAE 90.1 on reheat stuff, I assume they talk about that in there. We rarely run into that condition in our climate so I am not familiar w/ what the energy code may say.