Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Air ionization-Effective technology to address odours? 1

Status
Not open for further replies.

MedicineEng

Industrial
Jun 30, 2003
609
Hi all:

I wonder if any has had any experience with ionizer technology to address obnoxious odours (cigarrete, kitchen).

Some people swear by it, others call it basically a marketing gimmick, so I'm kind of confused here.

We're in the middle of some test trials for FCUs in a smoking environment and I do feel a different smell next to the ionizers, but not sure how effective these are in breaking down the smells and actually make the air fresher.

What is your opinion?

 
Replies continue below

Recommended for you

"Ionizer" as compared to "electrostatic filter" are very different.

I'm not sure which you're really meaning.

Electrostatic filters tend to remove all particulates from an air flow - very effectively. If the smell is a part of the particulates then the smell will be removed also. Cigarette smoke is an example of that. We have a bowling alley in our town that back in smoking days, would make your eyes water and you couldn't see the full 25 lanes across. They put in four big electrostatic filters hanging from the ceiling evenly spaced down the width of the alleys and within minutes of turning them on no smoke was visible and you could hardly smell it. They ultimately had issues with the amount of putrid gunk ciggybutt smoke of that magnitude caused in the filters, and had to purchase more 'cells' so they could swap them out for weekly cleaning.

Most odors are organic compounds that electrostatic forces don't manipulate very effectively. Food odors and such are usually better handled by activated carbon filtration.

Ionizers can put a charge onto any particulates that float within they're influence. What results is like charged balloons - millions of tiny ones. They then get attracted to the oppositely charged surface and go stick there. This is like an electrostatic filter but with the capturing part of the filter being 'other things' in the vicinity. That's not very useful and can result in dirty nearby surfaces.

Ionizers often give off ozone which in small amounts besides being considered unhealthy tends to give people a "feeling of freshness" and may actually oxidize some of the odorants.

The sleazy method most often used is odor control systems. These systems put atomized chemicals that simply stop humans from smelling anything in their presence. They're quite effective often totally effective. They creep me out.

Keith Cress
kcress -
 
itsmoked:

Thanks a lot for your reply.

I'm pursuing several air quality issues at the same time and you might have seen my other thread on kitchen exhaust systems.

From what I understand, ionizers and EPs both generate ozone because they work on the same principle, isn't it?
 
EPs and ionizers are NOT the same as ozone generators. Ozone will chemically combine with the odors, oxidizing them to a harmless state. Thus, the odors are eliminated, not just masked. I worked on a project at an airport parking garage that also housed dumpsters. The ozone generators added worked when nothing else would. Odors gone, no more complaints.
 
Smokers are people too. For the room to which you condemn these people, it need only have slightly more exhaust than supply. If you want to provide 400 cfm to cool the space (although the smokers may not deserve cooling of any sort), exhaust 600 cfm. Scrubbers, precipitators, carbon or HEPA need not apply.
 
Status