Airflow checking

Status
Not open for further replies.

redif

Mechanical
Dec 25, 2003
8
Hi,

We are designing a fan and duct system. The rooms should always be ventilated. As per our client's requirement, if there is a reduction in airflow ( due to any fault), it has to be signalled at remote controlled station. There are two ways to send signal to remote station.

1. By providng pressure switch in the duct, so that if there is reduction in airflow, PS will sence the reduction in static pressure and give signal to remote station.

2. By sensing the motor amperage. if there is big fluctuation in amperage it will be signalled to remote station.

Can anybody tell the better system out of two.

Thanks
 
Replies continue below

Recommended for you

I recommend using (2) fans with one as backup. Each fan should have a differential pressure switch, automatic intake damper and automatic discharge damper. The DPS should be between the fan inlet & outlet. I prefer DPS versus current sensors because it will sense belt failure. Some CT can sense belt failure but it must be provided at each phase if motor is 3 phase.
 