I have two basic questions regarding the Seismic Provisions for Structural Steel Buildings if one is dumb enough to try an ASD design method.
Question 1: To do a "traditional" ASD design, is it correct to design to ASD load combinations (i.e. 0.7E) and then decrease the load by the prescribed 1.7 multiplier and then increase the load by the appropriate ASD "phi" factors per this document? For example, a column with (simplistically only) a 100 kip (ultimate) seismic force would be designed for:
0.7 * 100 / 1.7 / 0.85 = 48 kips = design load for ASD.
This is what I interpret this document to say and the 0.7 combined with the 1.7 seems too liberal to me. Are they embedding the old (forbidden now) 1.33 stress increase with this?
Question 2: How does one treat the load to capacity ratios that are referenced in this document? For example, for a SCBF, one needs to consider Pu/(phi Py) for the column design forces (E vs Em). How do you do this with ASD and service loads? Does one ratio service loads (not ultimate) to nominal capacities as modified in my first question or do you have to run ultimate load combinations to determine Pu?
I will thank folks in advance for any advice given.
Question 1: To do a "traditional" ASD design, is it correct to design to ASD load combinations (i.e. 0.7E) and then decrease the load by the prescribed 1.7 multiplier and then increase the load by the appropriate ASD "phi" factors per this document? For example, a column with (simplistically only) a 100 kip (ultimate) seismic force would be designed for:
0.7 * 100 / 1.7 / 0.85 = 48 kips = design load for ASD.
This is what I interpret this document to say and the 0.7 combined with the 1.7 seems too liberal to me. Are they embedding the old (forbidden now) 1.33 stress increase with this?
Question 2: How does one treat the load to capacity ratios that are referenced in this document? For example, for a SCBF, one needs to consider Pu/(phi Py) for the column design forces (E vs Em). How do you do this with ASD and service loads? Does one ratio service loads (not ultimate) to nominal capacities as modified in my first question or do you have to run ultimate load combinations to determine Pu?