AISC Manual (13th Ed.) Table 3-6, Max. Total Uniform Load

Status
Not open for further replies.

palves

Structural
Jun 6, 2008
61
0
0
US
Does anybody out there use this table? I decided to check it out recently, but it doesn't seem to be very user friendly. A few questions.

-Why do they bill it as a "Uniform" load table when they give it to you in kips? Assuming it means kips/foot will give you a moment far higher than the allowable.

-What exactly is the Wc (Uniform load constant) and why is it in k-ft? I've never seen this variable before.

If there is some insight out there I'd love to hear it. Thanks.
 
Replies continue below

Recommended for you

Don't have the AISC handbook in front of me, but assuming it's the same concept as the CISC tables then it's expressing the total applied load (i.e. [load/unit length] x span ).

So if you see 100kN as the load at a span of 2m it's a total load of 100kN spread uniformly over 2m or 50kN/m across the whole beam. I'm betting there's a series of diagrams in there somewhere that tell you what the equivalent tabular load is for a variety of different load conditions.
 
I find every engineer uses these tables in one form or another.

Recently I have been asked by fabricators to design connections for given project and every send of engineering drawings references using 1/2 UDL to design connections on beams where the load is not given at the end of the beam. It's frustrating to have a 3' long W12x14 that has a UDL of 85.6k meaning I need to design the connection to resist 42.8 kips.

All the answers to the questions you are asking can be found on page 3-27.
 
Beware that the notes concerning Wc on page 3-27 in AISC_13 are not correct. Errata from Feb 3, 2009 states:

The 4th paragraph should read, “The uniform load constant, φbWc or Wc/Ω (kip-ft),
divided by the span length, L (ft), provides the maximum total uniform load (kips) for a
braced simple-span beam bent about the strong axis.”
 