Motor Insulation class is F with B temperature rise.
The Motor vendor recommends to set the alarm / trip value at 140 degree Celsius and 155 degree Celsius respectively.
Max Ambient temperature at Site: 45 degree Celsius
The vendor says if alarm / trip value set at 120 degree / 130 degree, the PT 100 will constantly trigger alarm and trip often.
This is not typical of what I'm accustomed to, as we typically set the Alarm / trip value at 120 degree Celsius and at 130 degree Celsius respectively for Class F/B motor insulation class.
So I asked the vendor to set at 120 degree / 130 degree, he comes back with a variation order saying it is a design change.
I think what I asked is quite typical. Any reason for vendor's argument?
The Motor vendor recommends to set the alarm / trip value at 140 degree Celsius and 155 degree Celsius respectively.
Max Ambient temperature at Site: 45 degree Celsius
The vendor says if alarm / trip value set at 120 degree / 130 degree, the PT 100 will constantly trigger alarm and trip often.
This is not typical of what I'm accustomed to, as we typically set the Alarm / trip value at 120 degree Celsius and at 130 degree Celsius respectively for Class F/B motor insulation class.
So I asked the vendor to set at 120 degree / 130 degree, he comes back with a variation order saying it is a design change.
I think what I asked is quite typical. Any reason for vendor's argument?