All: How can I calculate power c

Status
Not open for further replies.

npf

Chemical
Jul 16, 2003
66
All:

How can I calculate power consumed by flow controllers-

I have flow controllers installed on the air, water and fuel gas line going to the heater well.

Your help would be appreciated

-npf

 
Replies continue below

Recommended for you

You try looking in the datasheet?

TTFN

FAQ731-376
 
What kind of flow controller? Are you dealing with individual 4-20 mA loop controllers, DCS, PLC, or what? Clarify your needs.

Assume that each loop requires 20 mA at 24 Vdc for the transmitter and the current to pneumatic converter. Without considering anything load for the controller itself you use about a Watt per loop. Let's play with a throw-down cabinet based upon some wild but conservative assumptions.

For a throw-down example, a full DCS cabinet with a serious multiple loop controller and I/O cards to accommodate about 96 loops may require a power supply with a dedicated 20 Amp circuit that accommodates up to 16 Amps AC load at 120 VAC. The power supply may only provide 30 or so Amps at 24 VDC. Let's say that this multi-loop controller and cabinet includes three racks of I/O boards with eight cards per chassis and eight points per card. Each loop requires two points. Based upon the power supply capacity in AC Watts, this throw-down cabinet load is just under 2000 Watts, about the same as a toaster oven. My three racks with eight cards and eight points works out to 192 points or 96 loops. Typically we only permit up to about 80% capacity but the excess may be in the next cabinet. At 96 loops that is about 20 Watts per loop. Round up if identifying circuits or HVAC loads. Perhaps 25 Watts per loop is a rational guestimate. The reality could be somewhat less.
 