We have:
A) 1762-L24AWA Micrologix 1200 PLC
B) 1761-CBL-PM02 Ser. C Cable (Serial to PLC)
C) AB 9300-USBS Adapter (USB to Serial) with Prolific Software/Driver
D) RS LInx Classic Rev. 2.50.00.20
E) RSLogix 500 Rev. 7.00.00 (CPR 7)
F) HP Pavillion 8330 Computer (only has USB Ports)
1) With the HP 8330 Computer using USB Adapter I can connect to the PLC
Driver Type: RS-232-DF1
Device Name: AB_DF1-1 Device: SLC-CHO/Micro/Panelview
Comm Port: COM 4 Station Number: 00
Baud Rate: 19200 Error Checking: CRC
Parity: None Protocol: Full Duplex
Stop Bits: 1
These were obtained by the "auto configuration" function in the software.
1) I can connect to the PLC for a short period of time.
In the RSWho-1 Screen (RSLinx) On auto browse at the start it will show node 0 found (computer) and alternate to node 1 found (PLC). They willl alternate back and forth.
It will stay connected for a matter of minutes up to 10 minutes or so. As time goes on it will not show node 1 found. Then it looses the connection and goes off line.
Then come the Timeouts, ACK/NAK Timeouts, Retries, ENQ's Received, NAK's Sent and Packets Cancelled. Then Comm error 00005.
2) Searching the AB Knowledgebase I found that AB has a problem with the dual core processors. They are aware of the problem. A patch has been developed for use with a PCMK card. No patch is available for the USB adapter.
3) One of their suggestions was to turn off one of the processors. According to HP this is not possible.
Has anyone found any other way to fix this problem??
Thanks in Advance!
A) 1762-L24AWA Micrologix 1200 PLC
B) 1761-CBL-PM02 Ser. C Cable (Serial to PLC)
C) AB 9300-USBS Adapter (USB to Serial) with Prolific Software/Driver
D) RS LInx Classic Rev. 2.50.00.20
E) RSLogix 500 Rev. 7.00.00 (CPR 7)
F) HP Pavillion 8330 Computer (only has USB Ports)
1) With the HP 8330 Computer using USB Adapter I can connect to the PLC
Driver Type: RS-232-DF1
Device Name: AB_DF1-1 Device: SLC-CHO/Micro/Panelview
Comm Port: COM 4 Station Number: 00
Baud Rate: 19200 Error Checking: CRC
Parity: None Protocol: Full Duplex
Stop Bits: 1
These were obtained by the "auto configuration" function in the software.
1) I can connect to the PLC for a short period of time.
In the RSWho-1 Screen (RSLinx) On auto browse at the start it will show node 0 found (computer) and alternate to node 1 found (PLC). They willl alternate back and forth.
It will stay connected for a matter of minutes up to 10 minutes or so. As time goes on it will not show node 1 found. Then it looses the connection and goes off line.
Then come the Timeouts, ACK/NAK Timeouts, Retries, ENQ's Received, NAK's Sent and Packets Cancelled. Then Comm error 00005.
2) Searching the AB Knowledgebase I found that AB has a problem with the dual core processors. They are aware of the problem. A patch has been developed for use with a PCMK card. No patch is available for the USB adapter.
3) One of their suggestions was to turn off one of the processors. According to HP this is not possible.
Has anyone found any other way to fix this problem??
Thanks in Advance!