Delchi
Structural
- Apr 27, 2009
- 30
I have been pondering allowable deflection limits for our residential design standards for high-end residential *FLOORS BEAMS*(wood framed with LVL, glu-lam, and steel beams). I am trying to develop a list of criteria for younger engineers, and I would appreciate some input from some of y'all. Over time, I have tended toward the following limits for these expensive homes (using the minimum of any of the following):
Limit 1: Live load deflection less than L/360 for L < about 8 ft, L/480 for longer spans.
Limit 2: Total load deflection less than L/240 for L < about 8 ft, L/360 for longer spans, but never more than 3/4".
Limit 3: Beams parallel to a wall below: Total load deflection < 2D/240 max, where D is the distance from the beam to the adjacent wall.
Limit 4: Any beam supporting masonry: Total load deflection less than L/600.
I would appreciate some of your thoughts on these criteria, and any experience you've had with other types of deflection limits. Thanks!
Limit 1: Live load deflection less than L/360 for L < about 8 ft, L/480 for longer spans.
Limit 2: Total load deflection less than L/240 for L < about 8 ft, L/360 for longer spans, but never more than 3/4".
Limit 3: Beams parallel to a wall below: Total load deflection < 2D/240 max, where D is the distance from the beam to the adjacent wall.
Limit 4: Any beam supporting masonry: Total load deflection less than L/600.
I would appreciate some of your thoughts on these criteria, and any experience you've had with other types of deflection limits. Thanks!