digitrex
Electrical
- Mar 29, 2004
- 92
I have a difficult situation at this moment whereby a 6.6kV 3.1MW(FLC=320A) is needed to operate at a current just beyond 320A and upto 325A. This motor is driving a gas compressor. Unusual fluctuation of gas composition (increase in nitrogen content) lead to this higher load.
This motor has RTD in its windings and an overtemperature alarm and trip relay at the motor starter, but there is no digital display of the temperature. We manually connect a portable temperature meter to the RTD and found the temperature is around 105deg.C.
The overload relay setting had been re-adjusted to 328A.
We have to read the ammeter every 30min interval in order to be assured there is no sudden overload but this exercise may worn us down.
I now have the following plans and asking for your opinions whether I can safely do these and any other suggestions:
1. There 3 spare RTDs in the motor windings which I plan to install temperature transducers and have the temperature readings display in the Control Room computer screen such that it will generate alarm at 120deg.C (Class F insulation) and it will allow temperatures to be continuously trended.
2. With the ability of continuously monitoring the motor winding temperatures on the computer screen, I will increase the overload protection setting to 105% (or 336A).
This motor has RTD in its windings and an overtemperature alarm and trip relay at the motor starter, but there is no digital display of the temperature. We manually connect a portable temperature meter to the RTD and found the temperature is around 105deg.C.
The overload relay setting had been re-adjusted to 328A.
We have to read the ammeter every 30min interval in order to be assured there is no sudden overload but this exercise may worn us down.
I now have the following plans and asking for your opinions whether I can safely do these and any other suggestions:
1. There 3 spare RTDs in the motor windings which I plan to install temperature transducers and have the temperature readings display in the Control Room computer screen such that it will generate alarm at 120deg.C (Class F insulation) and it will allow temperatures to be continuously trended.
2. With the ability of continuously monitoring the motor winding temperatures on the computer screen, I will increase the overload protection setting to 105% (or 336A).