kevd
Electrical
- Nov 1, 2002
- 18
We are commissioning a 25MVA, 4160V brushless 2-pole alternator driven by a gas turbine at 60Hz (3600rpm). Today at with the gas turbine at synchronous speed and alternator off the bars the excitation was powered up for the first time. The AVR/excitor commissioning team set the manual excitation on its lowest setting, but when the excitation was switched on the excitation power convertor fully phased forward and the terminal voltage shot up to 1.5 x rated voltage. The excitation was shut off after 5 seconds and the set ran down to stop. It appears, according to the AVR commissioning engineer, that the phase rotation from the alternator PMG into the power convertor was wrong, hence the power bridge phased forward out of control. The gas turbine engineers reckoned we drew 2.5MW out of the turbine during the incident.
My question is this?
1. What damage could we have done to the set (insulation, rotor heating, etc.)?
2. What checks should we undertake to ensure the alternator is OK to resume commissioning?
3. How can we draw 10% power from the prime-mover when nothing is connected to the stator terminals, i.e. generator open loop?
Any help appreciated.
Kevd
My question is this?
1. What damage could we have done to the set (insulation, rotor heating, etc.)?
2. What checks should we undertake to ensure the alternator is OK to resume commissioning?
3. How can we draw 10% power from the prime-mover when nothing is connected to the stator terminals, i.e. generator open loop?
Any help appreciated.
Kevd