apowerengr
Electrical
- Jul 19, 2006
- 208
Does anyone have experience with 3" AL pipe bus splitting along its major axis for 1-3'? This is not a welded joint, the installations are outdoor, open air bus supported at 20' spans, no other mechanical loads exist, connectors are bolted-mechanical connections with aluminum bolts which were torqued per specs, the pipe is not deformed or oblong, no significant through faults have been experienced, load is not more than 50% of the rating of the bus per Alcoa tables, there are not end plugs in the pipe so water ingress/freezing should have plenty of room to expand without splitting the pipe.......I don't know what to think.
The visible splits are on the bottom of the pipe with the gap at the split 1/4" wide.
The installation is approximately 20 years old.
So I'm thinking can the splits just be welded or does the bus have to be replaced?
Any thoughts are appreciated.
The visible splits are on the bottom of the pipe with the gap at the split 1/4" wide.
The installation is approximately 20 years old.
So I'm thinking can the splits just be welded or does the bus have to be replaced?
Any thoughts are appreciated.