Gents
I need to add a PQM to my 11kV board to give me a kW value I can use for comparison purposes, I'm not looking for fiscal accuracy.
The 11kV switchboard I've inherited has CL 0.2S metering Cts used by the supply utility for fiscal measurements.
As part of the inheritance and already installed to the CL 5P10 protection Cts is an ammeter in the yellow phases and a GEC IStat in the red phase to give me an analogue signal for our measurements.
Before opening the board my intentions were simply to drop the new PQM in series with the Utility Companies fiscal meters.
Connecting into the protection relay Cts would still give me the accuracy I need without the possible polical fallout with the Utility Company but everything tells me this is a bad thing to do. The protection relays are supplying to a 50/51 O/C E/F protection relay.
Would value your thoughts
I need to add a PQM to my 11kV board to give me a kW value I can use for comparison purposes, I'm not looking for fiscal accuracy.
The 11kV switchboard I've inherited has CL 0.2S metering Cts used by the supply utility for fiscal measurements.
As part of the inheritance and already installed to the CL 5P10 protection Cts is an ammeter in the yellow phases and a GEC IStat in the red phase to give me an analogue signal for our measurements.
Before opening the board my intentions were simply to drop the new PQM in series with the Utility Companies fiscal meters.
Connecting into the protection relay Cts would still give me the accuracy I need without the possible polical fallout with the Utility Company but everything tells me this is a bad thing to do. The protection relays are supplying to a 50/51 O/C E/F protection relay.
Would value your thoughts