Ammonia Discharge

Status
Not open for further replies.

wfn217

Chemical
Aug 11, 2006
101
Regarding ammonia release from pressure relief valves, ASHRAE 15 says you can discharge to the atmosphere or to a tank with water in it. Is it required to report a relief valve discharge if you use the water tank option? Where can I find information to design the water tank.
 
Replies continue below

Recommended for you

wfn217:

Its been a very long time since I designed a couple of those water tanks. As I recall, the tank had to contain enough water to complete dissolve the entire in-plant inventory of ammonia and it needed to have a method for the safe disposal of that water after a relief valve discharge. As I also recall, the local fire department (at least in Los Angles, California) had some regulatority authority over such tanks.

As for reporting a discharge into a tank, I don't know. Perhaps you should contact your local air pollution regulatory agency and your local fire department.

Milton Beychok
(Visit me at www.air-dispersion.com)
.

 