Ampacity of Bundled Conductors 2

Status
Not open for further replies.

Mbrooke

Electrical
Nov 12, 2012
2,546
Anyone know how to properly calculate the actual current rating of twined Drake, Cardinal, Pheasant and Falcon? When designing new circuits under 345kv is there any advantage to twin vs single conductors? Also what risk is there in operating line hardware above 100*C (in 35*C ambient sun + 2ft/sec wind) 6-8 hours of the day about half the year?
 
Replies continue below

Recommended for you

Thanks!

Look like the program is based off PJM's values- which is good!
 
Above 230kV, the allowable conductor surface gradient becomes one of the governing factors in conductor selection. RUS Bulletin 1724e-200 recommends that max conductor gradient shall not exceed 16kV/cm. Using 795 drake as an example on 230kV line, you will get 15.9kV/cm conductor gradient. As conductor surface gradient is the function of line to line voltage, you will probably need bundle configuration on lines of 230kV or higher voltage levels.
 

The twin cable is twice the ampacity as a single cable as shown in the edited graph and table below.
To close match the circuit breaker or transformer FLC, it is customary to use a twin conductor for many applications up to 230 kV. This allows maximizing the system capacity for any future use without letting the conductor be the limiting factor.
One of the major concerns is to violate the NESC clearance do to excessive line sagging. Another concern is to have permanent conductor deformation or annealing the aluminum that may compromise the strength integrity of the line.

>>>>>>
ACSR_Cable_Ampacity_vvf4n3.jpg
 
Can you upload that graph? I'm having trouble seeing it. (sorry)
 
@KillBill7: Do you have link and what page? I've been wrong all along. This is why I love learning.
 
Exactly what I was looking for! Much Thanks! :)
 
Mbrooke,

Per your request, enclosed is the upload edited graph indicating the thermal behavior of the ACSR conductor under the conditions indicated.

Beware that this graph is a simplified approach that provides a rough performance of the ACSR cables.

I hope this became more clear in pdf format.

[URL unfurl="true"]https://res.cloudinary.com/engineering-com/image/upload/v1588344962/tips/ACSR_Ampacity_Graph_nocuif.pdf[/url]
 
Much appreciated. :) It is finally clear.

What are you getting for Bluebird BTW? Sag aside I'm at 1,600 amps 100*C, 35*C ambient sun+win.

Am I also correct to assume some annealing from STE loading is ok? I'm reading that the steal would not be effected and compensate for the 10% loss of AL strength provide this is originally factored in during the line designing stage.
 