Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Ampacity Rating of ACSR and AAC versus Copper

Status
Not open for further replies.

Tomm01

Electrical
Jun 10, 2014
1
Most bare copper conductors (used in a substation) are rated with an ambient temperature of 40 Deg C and temp rises of 30, 40 and 50 Deg C. All the ACSR and AAC tables I've seen (like Southwire) rate them at 25 Deg C ambient and only a 50 Deg C rise. Why don't the two worlds match their rating basis? How can you get an accurate ACSR or AAC rating at 30 and 40 Deg C rise above 40 Deg C ambient?

Thanks
 
Replies continue below

Recommended for you

There are some manufacturers' catalogues indicating ampacity for AAC and ACSR for 40 oC ambient air. For instance:
In “Aluminum Electrical Conductor Handbook” 3rd Edition published by Aluminum Association, Washington, D. C., 1989
Section II Bare Aluminum Wire and Cable presents a table [Table 3-13] for different cables in 40 oC ambient, no sun and still air or 2ft/sec wind.
You can follow IEEE 738/2006 calculation way also taking into consideration sun exposure and wind. In annex B you'll find even a Basic written program.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor