Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

amperage draw 7.5 hp comp. motor 1

Status
Not open for further replies.

turboranger

Automotive
Sep 25, 2007
2
hello. new 7.5 hp compressor motor. trips magnetic switch intermittantly.
-32amp run rated.
-runs at (35amps-235v) . starts at (150amps-205)fuctuates 5-10 %.
-its was (175amps-190v)on start until I ran new wire from fuse box to comp.
-1960 building stucture.old wiring
-is 205v to big of a voltage drop on start. ?????
-or is the comp. drawing to much.???
-capacitors passed ohmn metor test

any suggestions. thanks george
 
Replies continue below

Recommended for you

What is the rating of Mag switch? What is the setting of mag trip?

Starting current of 6-7 times would be considered normal. Your mag-trip must accomodate that. Have you looked at table 430.52 in NEC?

 
What is the overload device set at? It can be as high as 125% of motor full load amperage if the motor has a service factor of 1.15 or more, or has a marked temperature rise of 40 deg C or more. If not, it should be not more than 115%. NEC 430.32 (B)(1).

Voltage drop depends on how long it stays down, but it doesn't look bad for short duration.
 
Thanks for your replys. Your the greatest, love learning. You steered me in the right direction. (NEC)all is to code and specs. Just bumped up the trip setting slightly. thank george.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor