If the truss under UDL is what we consider as a joist, then the Canadian code does not require consideration of moment for the top chord if the panel points are less than 2'.
For smaller 'trusses' the redundencies are so great that the secondary effects from bending become less significant. Without quantifying it, the more redundencies you put into a system, generally, the stronger it gets. Although the web members have small moments at each end, the effective length of them is reduced, increasing the compressive resistance. If you're looking at a large truss, then I would consider the moments.
Catch the following parts of S16.1 (Canadian Code):
Open-web steel joists shall be designed for loads acting in the plane of the joist applied to the compression chord, which is assumed to be prevented from lateral buckling by the deck. For the purpose of determining axial forces in all members, the loads may be replaced by statically equivalent loads applied at the panel points.
The compression chord shall be continuous and may be designed for axial compressive force alone when the panel length does not exceed 610 mm, when concentrated loads are not applied between the panel points, and when not subject to eccentricities in excess of those permitted under Clause 16.6.11.4. When the panel length exceeds 610 mm, the compression chord shall be designed as a continuous member subject to combined axial and bending forces.
The code also requires provision of a point load for floor and roof joists.