I have a question regarding sill plate anchorage requirements. The 2000IRC requires that the wood sill plate be anchored to the foundation with minimum 1/2" anchor bolts at maximum 6' on-center. I am concerned about basement walls that retain earth, but are NOT cantilever retaining walls. These walls are braced at the top by the floor framing, and at the bottom by the footing or floor slab. The sill plate is typically pressure treated southern pine, which is loaded perpendicular to the grain. For a permanent load, the durattion factor is0.9. Therefore, according to the NDS the strength of 1/2" bolt embedded in concrete with 1 1/2" sill plate is 400*0.9=360 pounds. If you have an 8' wall retaining about 6 feet of good soil, the force at the foundation to sill interface is approximately 230 plf assuming at-rest soil conditions. Therefore, a 1/2" bolt is required every 1.57 feet. A 5/8" bolt would be required every 2.2 feet, and a 1" bolt is theoretically required every 3'. The force on a bolt at 6' spacing is 1380 pounds.
What am I missing here? I know that basement walls are going in with 1/2" anchor bolts at 6' spacing, but they seem to be overstressed.