I wonder if somebody could help me to understand the design of anchor bolts, in tension, in concrete and provisions of ACI318-11. I am trying to understand Clause D3.3.4.3 for lets say the following case:-
Design of base plate and anchor bolts for a simple goal post (Steel Frame) supporting a load at mid span. I have carried out the following steps:-
i. Calculate the seismic load and multiply the seismic loads by 2, where 2 is an overstrength factor.
ii. Use ASCE07-10 load combinations to analyse the goal post. Worst case loading, resulting in worst uplift/tension is for load case 5b (1.2D + E + L + 0.2S)
iii. Design base plate using reactions from the load case mentioned in item ii above.
iv. Base plate with four bolts will be required. Aim to is to have a ductile design conforming to ACI318. ACI318 Clause gives 4 cases viz D3.3.4.3a, D3.3.4.3b, D3.3.4.3c or D3.3.4.3d. I am not sure which one is the more appropriate in my case. Could somebody help to understand/decide.
I think that clause D3.3.4.3b is more appropriate for my case. But I am not sure how to calculate the anchor design forces to satisfy requirements of this clause. Clause is copied below:-
“The anchor or group of anchors shall be designed for the maximum tension that can be transmitted to the anchor or group of anchors based on the development of a ductile yield mechanism in the attachment in flexure, shear, or bearing, or a combination of those conditions, and considering both material overstrength and strain hardening effects for the attachment.”
I have the following questions:
1. Does step i mentioned above satisfy requirement “considering both material overstrength and …”?
2. How can strain hardening be considered in calculations, is there any recommended method that could be used?
3. In the light of above clause is it right to consider that base plate should fail/yield prior to the yielding of the anchor bolts (Please read clause "The anchor …… shall be designed ….. based on the development of a ductile yield mechanism in the attachment")
4. What forces shall I use for the design of anchor bolts? Can I use reactions as obtained in step ii above
5. if reactions from step ii are used, then it means that “attachment” (which in this case is base plate) and the anchor bolt are designed for the same loadings/reactions. I think in this case I’ll not be able to satisfying the requirement “development of a ductile yield mechanism in the attachment”. Should the force for the design of anchor be greater that used for the design of base plate, thus ensuring that base plate yields first, but how would one decide on the design force for anchor bolts.
Design of base plate and anchor bolts for a simple goal post (Steel Frame) supporting a load at mid span. I have carried out the following steps:-
i. Calculate the seismic load and multiply the seismic loads by 2, where 2 is an overstrength factor.
ii. Use ASCE07-10 load combinations to analyse the goal post. Worst case loading, resulting in worst uplift/tension is for load case 5b (1.2D + E + L + 0.2S)
iii. Design base plate using reactions from the load case mentioned in item ii above.
iv. Base plate with four bolts will be required. Aim to is to have a ductile design conforming to ACI318. ACI318 Clause gives 4 cases viz D3.3.4.3a, D3.3.4.3b, D3.3.4.3c or D3.3.4.3d. I am not sure which one is the more appropriate in my case. Could somebody help to understand/decide.
I think that clause D3.3.4.3b is more appropriate for my case. But I am not sure how to calculate the anchor design forces to satisfy requirements of this clause. Clause is copied below:-
“The anchor or group of anchors shall be designed for the maximum tension that can be transmitted to the anchor or group of anchors based on the development of a ductile yield mechanism in the attachment in flexure, shear, or bearing, or a combination of those conditions, and considering both material overstrength and strain hardening effects for the attachment.”
I have the following questions:
1. Does step i mentioned above satisfy requirement “considering both material overstrength and …”?
2. How can strain hardening be considered in calculations, is there any recommended method that could be used?
3. In the light of above clause is it right to consider that base plate should fail/yield prior to the yielding of the anchor bolts (Please read clause "The anchor …… shall be designed ….. based on the development of a ductile yield mechanism in the attachment")
4. What forces shall I use for the design of anchor bolts? Can I use reactions as obtained in step ii above
5. if reactions from step ii are used, then it means that “attachment” (which in this case is base plate) and the anchor bolt are designed for the same loadings/reactions. I think in this case I’ll not be able to satisfying the requirement “development of a ductile yield mechanism in the attachment”. Should the force for the design of anchor be greater that used for the design of base plate, thus ensuring that base plate yields first, but how would one decide on the design force for anchor bolts.