shau1
Civil/Environmental
- Dec 12, 2005
- 1
Question is about supplementary reinforcement suggested by ACI. This is for a column supposed to be "Fixed" to foundations.Axial load is 16870 lbf(uplift) and moment is 155413 lbf.ft. Using a baseplate 20"x20"x1 5/8", I need 10/12 Nos.
1 1/8" dia bolts and also need about 18" of embedment depth.
The pier size is restricted to about 24". Full breakout
capacity of 35 degree prism can not be mobilised because of close spacing. ACI says that calculations for breakout capacity is not needed if supplementary reinforcement
connecting the potential failure surfaces of breakout prism
to lower parts of structure is provided. Are these supplementary rebars for developing the uplift forces in the
anchor bars ? If so then can I compute the bond/development length by using usual equations for bond
length ?