LoneStarEngineer
Structural
- May 4, 2016
- 37
In Hilti Profis, the process of calculating shear capacity for anchors sitting on grout follows ETAG 001 Annex C (European guideline- Considers flexure in Anchor). While section D.6.1.3 Appendix D of ACI 318-11 just requires the shear capacity to be multiplied with 0.8 when a grout pad is used. The difference in shear capacity with a decent shear load (21k) on a sample anchor assembly results in a factor of 5 between the two procedures (With ACI being less conservative).
What are your thoughts on this?