crank71
Electrical
- Jan 6, 2005
- 3
We have a SR750 relay that when tripped activates an 86 lockout relay. Problem being that when the utility experiences a system sag, we go down on undervoltage or loss of phase and have to send an operator out to manually reset the 86. Ideally we want to have the 750 initiate a 86 lockout except when seeing an undervoltage/phase loss condition. In those situations we just want to trip the breaker and allow for remote re-close. Our schematic shows that the 86 coil and the breaker trip coil are in parallel so I think we'll have to change that and possibly assign the undervoltage and phase loss functions to a different 750 output that trips the breaker trip coil only??? and then have all other trips going to the 86 with a set of contacts in the breaker trip coil circuit....any other ideas much appreciated.