Hi all,
With a colleague I'm having a discussion on how to interpretarte the API 520 Part II recommendation of not having more than 3% pressure loss at the inlet piping to the PSV. I'm already aware of the following: “The calculation should contain only NON-RECOVERABLE losses. For gases, you DO NOT include acceleration losses as these are recoverable losses. Frictional losses in piping (including entrance and exit losses), fittings and valves, equipment and rupture disks if there was any are the only losses you need to consider. This means you should only be using the incompressible flow equation (i.e. Darcy) in calculating the piping losses.” Which is clearly explained in threat
Due to this 3% loss recommendation, you often have to "oversize" the piping to a larger diameter than the actual inlet connection diameter of the safety valve. In our case, we are having a 3" inlet pipeline to the safety valve, but the safety valves inlet connection is 1 1/2" (enough capacity for the relief case we have). Medium is natural gas (compressible fluid), set pressure 10barg. At the very end of the inlet piping we need a concentric reducer 3" x 1 1/2" to be able to install the valve.
In our flow calculations, the pressure drop of the inlet pipe is now mainly caused by the concentric reducer and just a little bit by the 3" pipe (which is a pretty long pipe in this case due to the vessel's double wall design). The concentric reducer is already causing approx. 3% of the pressure drop according our flow calculation.
In these pressure loss calculations, do you normally include the final reducing element to fit the safety valve as part of the inlet piping? Or can this be considered as "part of the safety valve"? I have to add to this that this case concerns a conventional safety valve, not pilot operated or balanced.
Thanks in advance for the feedback!
With a colleague I'm having a discussion on how to interpretarte the API 520 Part II recommendation of not having more than 3% pressure loss at the inlet piping to the PSV. I'm already aware of the following: “The calculation should contain only NON-RECOVERABLE losses. For gases, you DO NOT include acceleration losses as these are recoverable losses. Frictional losses in piping (including entrance and exit losses), fittings and valves, equipment and rupture disks if there was any are the only losses you need to consider. This means you should only be using the incompressible flow equation (i.e. Darcy) in calculating the piping losses.” Which is clearly explained in threat
Due to this 3% loss recommendation, you often have to "oversize" the piping to a larger diameter than the actual inlet connection diameter of the safety valve. In our case, we are having a 3" inlet pipeline to the safety valve, but the safety valves inlet connection is 1 1/2" (enough capacity for the relief case we have). Medium is natural gas (compressible fluid), set pressure 10barg. At the very end of the inlet piping we need a concentric reducer 3" x 1 1/2" to be able to install the valve.
In our flow calculations, the pressure drop of the inlet pipe is now mainly caused by the concentric reducer and just a little bit by the 3" pipe (which is a pretty long pipe in this case due to the vessel's double wall design). The concentric reducer is already causing approx. 3% of the pressure drop according our flow calculation.
In these pressure loss calculations, do you normally include the final reducing element to fit the safety valve as part of the inlet piping? Or can this be considered as "part of the safety valve"? I have to add to this that this case concerns a conventional safety valve, not pilot operated or balanced.
Thanks in advance for the feedback!