sandstars
Chemical
- Jul 19, 2012
- 3
I have 2 PSVs that protect the same vessel. One is 2J3, the other is 6R8. The vessel in question has a MAWP of 75 psig and both valves are set at 75 psig. We are running up against the relief flow rate (calculated using API 520 and 521 at 116% overpressure) and the lift pressure of the valves so my problem is twofold.
Without going in to a long, detailed discussion of the system setup, trust me when I tell you this: Due to a modulating valve, increasing the pressure set point on the larger valve will give us additional room for pressure whereas increasing the pressure on the small PSV gets us nothing from a pressure standpoint. We are currently running around 60 psig but plan to increase flow rate, which will subsequently increase the pressure of the system.
So, while parusing API 520, I ran across this little tidbit (paraphrased): "In multiple relief systems, the first device must be set at the MAWP. However, the second device may be set 5% higher." To kill two birds with one stone, I would like to increase the spring set point on the larger valve. API doesn't mention anything about different sized valves that I could find and I did not bother to dig through the ASME code yet that API references for this section. The feedback I've gotten internal to my company is that it's not the "conservative" approach and increasing the smaller one by 5% would be preferable even though that gets me nothing from a pressure standpoint and I would still have to add PSVs to the system anyway.
However, to their point, what's to stop someone from sizing a really tiny relief, calling that the primary, then sizing the larger one at 5% higher? Is this still acceptable per code? Does API assume both valves are sized equally for the 5% case to be true?
Thanks!
Without going in to a long, detailed discussion of the system setup, trust me when I tell you this: Due to a modulating valve, increasing the pressure set point on the larger valve will give us additional room for pressure whereas increasing the pressure on the small PSV gets us nothing from a pressure standpoint. We are currently running around 60 psig but plan to increase flow rate, which will subsequently increase the pressure of the system.
So, while parusing API 520, I ran across this little tidbit (paraphrased): "In multiple relief systems, the first device must be set at the MAWP. However, the second device may be set 5% higher." To kill two birds with one stone, I would like to increase the spring set point on the larger valve. API doesn't mention anything about different sized valves that I could find and I did not bother to dig through the ASME code yet that API references for this section. The feedback I've gotten internal to my company is that it's not the "conservative" approach and increasing the smaller one by 5% would be preferable even though that gets me nothing from a pressure standpoint and I would still have to add PSVs to the system anyway.
However, to their point, what's to stop someone from sizing a really tiny relief, calling that the primary, then sizing the larger one at 5% higher? Is this still acceptable per code? Does API assume both valves are sized equally for the 5% case to be true?
Thanks!