jamesbanda
Chemical
- Sep 21, 2004
- 223
I'd like a quick check on methods for fire area that should be used under API521 to get overall duty..
I believe if we have a system with two vessels the correct way to consider fire load is as below.
method 1: Q (Total) = 43.2 * F* A1 ^0.82 + 43.2 * F* A2 ^0.82
method 2: i believe this is incorrect.. QTotal = 43.2 * F* {A1+A2} ^0.82
for a vessel with area 50m2
Method 1 gives ~2100 KW
Method 2 gives ~1900 KW
So i believe method 1 is correct. thats what i've been using..but i've come across a calc the other way.. so wanted to check..