Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

API 650 - Air leak test on Bottom Sump, Manhole reinforcing and Nozzle reinforcing 1

Status
Not open for further replies.

pkloo80

Mechanical
Apr 28, 2013
4
Hi,

I had a doubt on my QC department that created a procedure of air leak test with below requirement:

Pressure: 1 bar
Holding time: 5 min
Additional: Soap solution

Can anybody here help me to clarify this requirement, Besides that I can't find any requirement on the 1 bar pressure with holding time of 5min in API 650.

Thank
Marvin
 
Replies continue below

Recommended for you

There is no specific requirement in the code for the reo pads leak test. The 1 bar seems a bit high, but it should work. 5 minutes to go all around the welds with soapy solution also seems a bit longer than required but hey, better do it twice around than missing a leak. All seems reasonable. I can't comment on the sump, since I don't know what are you actually testing.
Cheers,
gr2vessels
 
API 650 7.3.4 Inspection of Reinforcing-Plate Welds
After fabrication is completed but before the tank is filled with test water, the reinforcing plates shall be tested by the Manufacturer by applying up to 100 kPa (15 lbf/in.2) gauge pneumatic pressure between the tank shell and the reinforcement plate on each opening using the telltale hole specified in 5.7.5.1. While each space is subjected to such pressure, a soap film, linseed oil, or another material suitable for the detection of leaks shall be applied to all attachment welding around the reinforcement, both inside and outside the tank.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor