I am currently working on an office building which contains a kitchen. The only info I could find for heat gains given by the appliances were 1,000 W for a microwave and not much for the range/oven. Each kitchen will contain a microwave and consumer type oven. Does anyone have good info or rule of thumb to use for the appliance heat gain in the kitchen? I also have found heat gains for a standard business copy machine listed as 1000-1500 W as well which seems high. I was planning on using about 200 W per desktop computer with monitor. Thank you for your input.
 
Replies continue below

Recommended for you

Is the kitchen equipment going in an office kitchen or were you gathering information form your own office kitchen? When I figure cooling loads for office kitchens, I don't count ovens or microwaves because they are so infrequently used. I do figure a 100W load for a standard refrigerator and 1500W for a coffee maker as these items are used almost all day.

If the oven is in a residence, I use AHSRAE value of 1600 Btuh.

The computer load of 200W per workstation seems high. I figure 150W and even that's on the high end. I figure it covers other minor items like clocks, printers, etc.
 
Yes, the equipment is going in an office kitchen. What you have done sounds pretty reasonable, is 1,500 W about right for a typical coffee maker? Just wanting to make sure that is not a typo. I did find similar info in ASHRAE books but it looks very outdated. Thanks.
 