iken
Mechanical
- May 13, 2003
- 151
Can any body please advise contact details for the Manufacturer (not a supplier) of these Cooling Towers.
My problem is that I have a supplier stating that these towers (MSS141A) will operate fine under these conditions.
Design Flow = 73 l/s
EWT 35 degC
LWT 29.5 degC
Ambient WB 22.5 degC
Heat Rejection 1700kW
This is not the problem. The prblem is there are 3 towers (or would be), and all towers will have water flow regardless of the chiller operation. Here's the problem. When only one chiller is operating, there would only be 64 l/s to serve all Towers (21.3 l/s each). Under this condition, we have been advised the towers will operate fine, and would expect that the tower efficiency (related to outpt) would be around 80%.
These numbers do not seem to be correct - reduce flow to 30% design, and towers will only reduce to 80% design.
Any help would be greatly appreicated.
My problem is that I have a supplier stating that these towers (MSS141A) will operate fine under these conditions.
Design Flow = 73 l/s
EWT 35 degC
LWT 29.5 degC
Ambient WB 22.5 degC
Heat Rejection 1700kW
This is not the problem. The prblem is there are 3 towers (or would be), and all towers will have water flow regardless of the chiller operation. Here's the problem. When only one chiller is operating, there would only be 64 l/s to serve all Towers (21.3 l/s each). Under this condition, we have been advised the towers will operate fine, and would expect that the tower efficiency (related to outpt) would be around 80%.