Arc detection relay Vs UFES (Ultra fast earthing switch)

NickParker

Electrical
Sep 1, 2017
434
The transformer specification states that "Transformer enclosures and cable connection boxes shall be designed in such a way that an internal arc will not pose any personnel risk to operators, even in the event of an arc fault."
After consulting with the vendor, they propose using a UFES (Ultra-Fast Earthing Switch) on the transformer enclosure, which can clear faults within 4ms. I am accustomed to using an arc detection relay in MV switchgear, which trips the breaker but takes longer—typically around 50 to 80ms.

I would appreciate your thoughts on using UFES versus an arc detection relay.
 