Hi, i have a 208 V panelboard fed by a 75 kva transformer which i want to calculate the Hazard Risk Category.
fault level: 4 kA
fault clering time : approx. 1 sec (the fault will be clear by the fuse at the transformer primary)
With the IEEE 1584 standard, it gave me PPE category 3. The 1584 doesn't work for 208V <125 kVA.
If i take the NFPA 70E table 130.7(c)(9)(a), in note 1 it is written " 25 kA available, 2 cycle clearing time". So it can't apply since the fault duration will be longer.
So no standard can apply in that situation. Am I missing something? Because 2 cycle clearing time in the NFPA70E is a little bit short. I don't know many circuit that will open in 2 cycle! What can i do, just put a warning label?
thanks