wbd
Electrical
- May 17, 2001
- 659
Hello,
I am currently working on a arc flash study on a system having multiple sources operating in parallel. This is providing some interesting results and I would welcome any comments.
Faulting a common bus, with both sources active, results in an incident energy of 268.7 cal/cm2. Faulting the same bus but only one source at time, results in 7.6 cal/cm2 for one source and 21.5 cal/cm2 for the other. I don't how the program arrived at the 268 number unless it took the higher arcing current but used the longer time time figure.
From the individual results, the worst case is 21.5 cal/cm2, so would it be correct that this would be what should be protected to?
I am currently working on a arc flash study on a system having multiple sources operating in parallel. This is providing some interesting results and I would welcome any comments.
Faulting a common bus, with both sources active, results in an incident energy of 268.7 cal/cm2. Faulting the same bus but only one source at time, results in 7.6 cal/cm2 for one source and 21.5 cal/cm2 for the other. I don't how the program arrived at the 268 number unless it took the higher arcing current but used the longer time time figure.