Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Arc Flash Evaluation for Single Phase Equipment

Status
Not open for further replies.

Dumbo2929

Electrical
May 31, 2005
109
I was wondering what people are doing as part of arc flash evaluations when you have both 3-phase and single-phase equipment (panels, etc.) My experience is that some arc flash software ignores single phase equipment and that it is somewhat ignored in NFPA-70E. It seems silly to have a HRC/PPE specific label on a 3-phase panel and have a single-phase panel right next to it with no label. Any thoughts?
 
Replies continue below

Recommended for you

Single-phase 240V panels are discussed in IEEE-1584. Their recommendation is to model them as an equivalent three-phase 240V panel. The IEEE-1584 arc-flash equations are all based on three-phase faults. The results should be conservative.



 
I can model them as 3-phase, but them I have to model the upstream transformers as 3-phase (75kVA vs. 25kVA for example). It just complicates things.
 
Dumbo,

The standard allows you to ignore xfmr's below 125kVA (480-208/120V systems).

Mike
 
Unfortunatley the customers typically require all panels to labeled.
 
You might want to go to:
They have arcflash shareware ("Duke Power Heat Flux Calculator") that allows for 120VAC calculations.

David Baird

Sr Controls Designer
EET degree.
Journeyman Electrician.
 
Yes, you have to model the transformers as three-phase as well.

IEEE-1584 recommends that ALL 240V systems be evaluated. For 208V systems, they recommend evaluation for systems 125 kvA and larger. 240V and 208V are treated differently.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor