I did some searching and reading through these forums before posting, and was unable to find an answer. If this topic has already been covered, I apologize and if a link could be provided I'll happily delete this post (can I do that? I'm new here) and go read the original thread.
That said, here's my question.
I'm working on a power study and arc flash analysis using SKM Power*Tools software for an approximately 200-bus system at a local plant. For the most part it's pretty straightforward - IEEE 1584 and NFPA 70E have been helpful, and the IEEE Red Book as well. However, there are several ties in the plant, including three at the 13.8kV level in the main electrical substations. The utility company feeds 161kV into the yard, where the plant has six transformers with OCB protection. Each transformer steps down to 13.8kV then feeds through a 13.8kV main breaker into switchgear. A tie breaker/bus is located between the switchgear in pairs (so 1 can be tied to 2, 3 to 4, and 5 to 6).
Now, I can calculate the arc flash at the main 13.8kV bus with no problem during normal operation (all ties open). I can also calculate with the tie breaker closed. However, it seems to me that there would always be a high flash value present in the tie breaker compartment because it has two energized buses at all times, fed by different transformers. If a fault occurred in the tie compartment, couldn't it have contribution from each bus?
My question is, would the tie compartment need to be labeled with the tie-closed flash label, or would it be a summation of the two tie-open flash values? It seems to me that the worst-case scenario would be a fault starting at one side of the open tie breaker, burning through almost its entire lifetime, then spreading enough to trigger a fault on the other side of the tie breaker from the other bus. In essence, two faults from two separate busses in one compartment. However, I'm not sure how likely that is. It seems more likely that the tie-closed flash value would be the value needed at a tie. I haven't been able to find any literature that discusses this scenario, though, and I'd love to find an IEEE or other standard to back me up on this.
If anyone can point me toward some literature, it would be very helpful. Or some discussion on the subject from more experienced engineers would be wonderful. I'm a year and a half out of school and this is the biggest project I've had so far.
Thanks in advance for any help, and sorry for the long-winded post!
That said, here's my question.
I'm working on a power study and arc flash analysis using SKM Power*Tools software for an approximately 200-bus system at a local plant. For the most part it's pretty straightforward - IEEE 1584 and NFPA 70E have been helpful, and the IEEE Red Book as well. However, there are several ties in the plant, including three at the 13.8kV level in the main electrical substations. The utility company feeds 161kV into the yard, where the plant has six transformers with OCB protection. Each transformer steps down to 13.8kV then feeds through a 13.8kV main breaker into switchgear. A tie breaker/bus is located between the switchgear in pairs (so 1 can be tied to 2, 3 to 4, and 5 to 6).
Now, I can calculate the arc flash at the main 13.8kV bus with no problem during normal operation (all ties open). I can also calculate with the tie breaker closed. However, it seems to me that there would always be a high flash value present in the tie breaker compartment because it has two energized buses at all times, fed by different transformers. If a fault occurred in the tie compartment, couldn't it have contribution from each bus?
My question is, would the tie compartment need to be labeled with the tie-closed flash label, or would it be a summation of the two tie-open flash values? It seems to me that the worst-case scenario would be a fault starting at one side of the open tie breaker, burning through almost its entire lifetime, then spreading enough to trigger a fault on the other side of the tie breaker from the other bus. In essence, two faults from two separate busses in one compartment. However, I'm not sure how likely that is. It seems more likely that the tie-closed flash value would be the value needed at a tie. I haven't been able to find any literature that discusses this scenario, though, and I'd love to find an IEEE or other standard to back me up on this.
If anyone can point me toward some literature, it would be very helpful. Or some discussion on the subject from more experienced engineers would be wonderful. I'm a year and a half out of school and this is the biggest project I've had so far.
Thanks in advance for any help, and sorry for the long-winded post!